biggsy said:Mine is a question as much as it is a suggestion, but does it meet code to terminate the dryer circuit at a sub-panel and then run two 30a circuits off of the sub-panel to the dryer and garage? Leaving the 30a breaker in the main panel to feed the sub would protect the line and as long as he didn't try to run both at the same time he would never trip the breaker. Depending on how the dryer circuit is currently run it may wind up costing more than running the new line if you are not comfortable doing it yourself.
Also, have you checked the dryer circuit, what gauge wire was used to the dryer. If it is not either 8 or 6ga I would suggest just running the new line and forget any other options.
I was mostly just wondering for future reference.
EDIT: After further thought, any attempted work around is going to cost a close to $200 and still have to worry about the circuit. Like smkettner said, pay the $500/600 and get it done right and be done with it or just use the 120v EVSE and live with it until you can afford or justify the expense.
Just a comment on the gauge of the wire. According to code if you have a circuit that has a constant draw over a long term like a heater, stove, dryer, or EVSE you need to de-rate the current capacity of the wire to 80% of what is normal.
This means that while a 10ga. wire will typically run 30a, if you are using it in this category it is only really good for 24a. So for a 30A breaker you need to go to 8ga. or better (8ga. - typically 40A de-rated to 32A).
Also, if you are buying the wire yourself you will find it pretty expensive when going to your local Home Depot or hardware store. However, if you go to an electrical supply house you will probably find it cheaper. (Odd note - local supply house would not sell it cut to length in the gauge I needed, but by going one size larger they would cut it for me and it came out cheaper. Saved about $30.