I am planning on installing a clipper creek HCS-40p. I'm reading in the instruction manual that "This is a single-phase device. Do not connect all three phases of a 3-phase feed!!!". It later says "A neutral connection is not reuqired by the HCS. Only Line 1, Line 2, and Ground are required". And later it says "Do not connect it to a neutral bar, or to ground".
Am I understanding this correctly, that in the outlet itself for the 14-50, I should only have the two hot's, and the ground connected in the plug? I'm having an electrician install the plug & wiring, so I want to make sure I communicate the specifics on what I need him to do. It also looks like the plug will need to be installed upside down (installing EVSE above outlet) - with the ground furthest away from the EVSE?
Am I understanding this correctly, that in the outlet itself for the 14-50, I should only have the two hot's, and the ground connected in the plug? I'm having an electrician install the plug & wiring, so I want to make sure I communicate the specifics on what I need him to do. It also looks like the plug will need to be installed upside down (installing EVSE above outlet) - with the ground furthest away from the EVSE?