TonyWilliams said:
Would there be any reason why I could not use two NEMA 14-50R outlets (at an RV park) and combine them into one box for 100 amp service ?
Disclaimer: This is not safe in the hands of a non-experienced user, but would be fine for Tony, and only if continuously supervised.
Take a 4 slot small subpanel, install two 50A breakers in there, connect your QC to the main bus. Connect two 14-50 plugs on cables, one to each breaker, (hot-hot) do not connect neutrals, but do parallel the grounds. Install four 240v pilot lamps, with the first two lamps across the same 2 legs on each of the 50A breakers, (14-50 sides) two more pilots the same way, except swapping the hots on one breaker. (X)
To confirm, the four pilot lamps are connected as follows:
Lamp1: leg 1 of breaker 1 and leg 1 of breaker 2
Lamp2: leg 2 of breaker 1 and leg 2 of breaker 2
Lamp3: leg 1 of breaker 1 and leg 2 of breaker 2
Lamp4: leg 2 of breaker 1 and leg 1 of breaker 2
To use: Verify all breakers OFF, Connect your 14-50's, and verify that you have this pattern of lights:
Off-Off-On-On
Then, and only then, is it safe close the breakers. If there is significant resistance difference in the circuits, you may have an imbalance that could trip circuits, so it might be worth carrying a clamp-on ammeter to verify.
If you have this pattern instead:
On-On-Off-Off
You need to simply swap the hots in one 14-50.
Any other pattern indicates the outlets are on different phase legs, on different power systems, or have one or more dead legs, so try others.
NEVER unplug any 14-50 unless all breakers are off!
This same box could be used with a single 14-50 outlet, setting the QC to pull under 50a, just only close the breaker of the cord in use.
This box could be made automatic and safe for general use by the addition of contactors and a control system, but it would get bulky, heavy, and expensive.
-Phil