Even with a 300+ mile range to replenish... a 50a connection would be fine at home. JMHO
smkettner said:Even with a 300+ mile range to replenish... a 50a connection would be fine at home. JMHO
Volusiano said:Even for a home scenario, I'll take the 6.6kW charger over the 3.3kW charger any day, because I don't ONLY charge overnight. I charge during the day, too, all the times, especially on the weekend, when the off peak rate applies all weekend long.
Size 8 awg is only rated up to 55A IF you have 90C insulation rating on your wire. Otherwise, it only has 40A rating for 60C insulation rating.ERG4ALL said:But the nice thing is that #8 ga. is rated up to 55A (Renewable Energy Handbook, pg. 550). Thus, if down the road you get a higher capacity charger, you won't have to replace the wiring. Because this is for overnight charging, I see no reason to put in larger wiring, #6 would allow up to 75A which in my opinion is overkill.
One possible misconception here. "Quick Charge" is Nissan's term for high voltage DC charging through the CHAdeMO port. 50A at 240v isn't nearly enough to utilize that fully. The most you can get out of that circuit is 9.6kW, which would take at least an hour and a half to go from low battery to 80%. But nobody is going to be putting chargers capable of 30 minute Quick Charges into their garages, so that is not a problem.jopeters41 said:Well, They have put in a 50 amp. 240v circuit. I took a a photo of the wiring , I want it to be ready for the next generation on of charging. Its a 6/3 stated on the wiring, what ever that means???????????????. Is this what I need for future quick charging,
That's a good start, but it's a bit more complicated than that.Volusiano said:Size 8 awg is only rated up to 55A IF you have 90C insulation rating on your wire. Otherwise, it only has 40A rating for 60C insulation rating.
Size 6 awg is only rated up to 75A at 90C insulation rating. Otherwise, it only has 55A rating for 60C insulation rating.
So unless you know for a fact that you have 90C insulation rating, don't assume that your #8 has 55A or your #6 has 75A. If you don't know your insulation rating, assume that it's 60C insulation and based on this, your #8 is only 40A and #6 is only 55A max.
Typically the lug in the equipment on which you terminate your wire will have a temperature rating on it. For simple equipment like an EVSE that should be the termination rating. The equipment spec sheet should also have that info. For a breaker, however, the termination rating is often lower than what is stamped on the lug and should be printed on the breaker body. That is because a circuit breaker is certified not to trip below its rated current at its rated operating temperature (typically 40C). To do this it depends on the length of wire terminated on it to act as a heat sink. So the breaker might use a lug stamped 90C, but the breaker body says the termination rating is only 75C or 60C.Volusiano said:By equipment termination rating at 75C, do you mean like the EVSE temperature rating?
I'd also recommend wiring for 240V/100A is you're building new and have the resources to do it. This will ensure you're future proof. I've been talking to some friends who are placing their reservation for a Model S Signature Edition next week and have been trying to figure out charging options.mitch672 said:smkettner said:50amp is good for the next generation and the third generation many years away.
If you happen to be in line for a Tesla Model S, I would wire a 90A or 100A circuit, and use a CS-90/CS-100, that will charge at the full 75A rate (18KW) that J-1772 is capable of, the initial Tesla Model S's are comming with a 300 mile pack, that could use it. Other than that 1 EV, 32A MAX (40 AMP circuit), will be good for anything else out there.
http://www.clippercreek.com/index.php?option=com_content&view=article&id=84&Itemid=164" onclick="window.open(this.href);return false;
http://www.clippercreek.com/documents/PDF/product_information/commercial/ClipperCreek%20CS%20Series%20Brochure.pdf" onclick="window.open(this.href);return false;
smkettner said:If you want to future proof you better have 100a for every possible vehicle you may own and for your visitors. So 100a x3 in a 3 car garage and maybe two circuits out front for a visitor (2 x 100a). Looks like 500a to me to be future proof. So that puts you at probably an 800 amp panel :shock:
Or you can be reasonable about it. But I would rather have three 40s compared to a single 100a.
mitch672 said:100A is a good choice to wire to a garage, just wire it to a subpanel, and from there install PVC pipe to a few spots for future EVSEs, could be a single 90A, or (3) 30A, or (2) 50A, etc. There is nothing wrong with being prepared. You can also install a dedicated 120V 20A, and an 20A dedicated L6-20R outside the garage for your future guests EVssmkettner said:Or you can be reasonable about it. But I would rather have three 40s compared to a single 100a.
Exactly Plus One. I am doing the plans for a remodel, and aim to relocate the electric drop right to the garage! This was my thinking for other reasons (will treat the current panel as a sub), but it means the mains will be right in the garage, and I will be set to do whatever is needed, included adding a TOS meter easily, and efficient use for power billed (minimum line loss).Devin said:mitch672 said:100A is a good choice to wire to a garage, just wire it to a subpanel, and from there install PVC pipe to a few spots for future EVSEs, could be a single 90A, or (3) 30A, or (2) 50A, etc. There is nothing wrong with being prepared. You can also install a dedicated 120V 20A, and an 20A dedicated L6-20R outside the garage for your future guests EVssmkettner said:Or you can be reasonable about it. But I would rather have three 40s compared to a single 100a.
Exactly. Rather than have 3x240V/40A lines run to your garage have a singled 240V/100A line to a subpanel and split from there as necessary. As in my 240V/60A situation this provides for an easy upgrade to a higher current charger than having to run new wire and also makes a much cleaner run from the electric panel to the garage. Seems much more reasonable than running 3 independent lines from your main panel.