Seems like this version would work nicely with a Bluetooth module and a smartphone. Display and control from the phone while maintaining a "plain" look to deter theft.
Okay, now I understand. The word, "balanced" was throwing me off, as might be used when referencing different phases in a 2 or 3 phase AC power distribution system, which could also be present to some extent even in a "split phase" 240V power circuit, correct? Is this possibly another reason why "two" fuses are needed instead of only one?AlanSqB said:It's unbalanced because in the situation described above, you could potentially have 50 or more amps flowing through components that are designed for a max of 30 amps.
If you are using 50A contactor, 50A rated cable and all other in-line components are rated for 50A, you don't need the fuses on the 50A circuit. That box, as sold, contains components only rated for 30A (relays) so it needs the fuses.
kubel said:The kit includes 4 locking washers. What are these to be used with?
As long as the conductors were sized correctly for a 40A breaker (i.e. #8 Cu conductors) and all connections were properly made up, the conductors were fine. The conductor ampacity is a continuous rating; it is the breaker that is not rated for the continuous load. So for a continuous load you have to upsize the breaker, but that of course requires upsizing the conductors, since the conductors need to be protected at or below their ampacity.dsinned said:By the time the CB tripped in the main distribution panel, it became VERY HOT; almost enough to burn my finger. Thankfully, it did its job, but I have no idea how hot the internal stranded copper wiring got from the breaker to the AC outlet, which is routed through the crawl space under the house and through a wall into my garage where that outlet is installed. I'd bet hot enough to be worrisome as I believe the dedicated wiring conductors are probably of insufficient gauge for a 40A continuous load. I wish I knew what the gauge size is for certain, but as I recall it is certainly not as large as 6AWG, which is recommended for a 50A outlet.
dsinned said:This issue keeps coming up with respect to these so-called "basic" kits. Current limiting seems to be sort of a "moving target" especially for "portable" units.
Personally, I don't care for Tesla's solution with resistor mods to a couple of common AC adapters. These cost $50 each. WAY overpriced imho! Not to mention, an adapter for 32A was completely omitted. These are quite commonly required, although there is no standard for "40A" outlets. Thus, many EVSE users are violating code with 50A outlets on less amperage circuits. I'm guilty of that as well!
I became concerned about this, so I did a "controlled" experiment last weekend. I intentionally increased the current limiter on my EVSE from 32A to 40A, which is easy to do with a JuiceBox with key fob and LCD options. I was charging my RAV4 EV with its OBC that allows a maximum of 10kW (or 250V at 40A). I measured ~225V AC line voltage at the EVSE at this load, so I was really only drawing about 9kW from the wall. As it turns out this presented a false sense of security!
On a moderately warm day, it took a little over 60 minutes for a 40A rated circuit breaker to trip in my Main Power Distribution Panel on the outside of my house. I purchased that breaker from Home Depot earlier this year, so I know it was essentially new and good condition. From the 50A outlet to the output cable of the EVSE, surface temperatures were all warm to the touch but not of any real concern. My Juicebox's I/O cables are rated for 50A/40A respectively, and the AC outlet rated for 50A it was plugged in to.
By the time the CB tripped in the main distribution panel, it became VERY HOT; almost enough to burn my finger. Thankfully, it did its job, but I have no idea how hot the internal stranded copper wiring got from the breaker to the AC outlet, which is routed through the crawl space under the house and through a wall into my garage where that outlet is installed. I'd bet hot enough to be worrisome as I believe the dedicated wiring conductors are probably of insufficient gauge for a 40A continuous load. I wish I knew what the gauge size is for certain, but as I recall it is certainly not as large as 6AWG, which is recommended for a 50A outlet.
This points out the inherent danger of using an L2 EVSE without an output current monitor display. These basic DIY kits are all well and good for the lowest cost, bare bones EVSE, but I highly recommend adding an output current monitor display for safety sake. Plus, make certain your circuit breaker protection is appropriate for the household wiring and J1772 output cable you are using, especially if you are using a 50A AC outlet to plug in your EVSE. Which ever has the lowest amperage rating, should match the rating of the circuit breaker. This is something that NO EVSE can determine for you, or warn you when it becomes overloaded, so you have to physically check it yourself. When in doubt, hire a qualified Electrician!
This is worth figuring out because #10 on a 40A breaker is not OK, while #8 is fine. If you can't read the insulation, go get a sample of #8 and of #10 and compare to the wiring in the breaker panel.dsinned said:I would guess #10 gauge wire; perhaps #8, but I'm just not sure.
In terms of voltage drop, 35' is fine for a 32A load on #8 copper.dsinned said:The length of the wiring is ~35' from the breaker to the EVSE's 50A outlet, so I think I could be on the hairy edge using it to charge my RAV4 EV at 32A.
By design, the conductor near the breaker acts as a heat sink for the breaker, so it will be hotter than the rest of the conductor. Therefore you may find it hot to the touch, but that doesn't mean there is problem.dsinned said:I'm going to check the surface temperature of the insulation where the wires are visible in the breaker box while charging at 32A. I'll do this for an hour or so, and if only ever warm to the touch, I think it will be okay.
kubel said:I got mine assembled today, plugged it in (120V) to test, and nothing. No LED, no relay checks clicking. I'm reading 120V across AC(L)and AC(N) on the power supply, so I'm assuming I didn't frak up at least to that point. How should I go about troubleshooting from there?
I also plugged in my old known working Open EVSE board and it fired right up, so I'm pretty sure it's all good up to the power supply. I'm just not sure how to test from there.
This sounds like the firmware on the new board needs to be reloaded; this happened to me once.kubel said:I got mine assembled today, plugged it in (120V) to test, and nothing. No LED, no relay checks clicking. I'm reading 120V across AC(L)and AC(N) on the power supply, so I'm assuming I didn't frak up at least to that point. How should I go about troubleshooting from there?
I also plugged in my old known working Open EVSE board and it fired right up, so I'm pretty sure it's all good up to the power supply. I'm just not sure how to test from there.
There are a number of issues with the comments made here. Firstly, code does allow for a 40A circuit on a 50A outlet. Of course, the device being used needs to comply with a 40A circuit. Secondly, your "controlled" experiment last week does not meet code. You have a 40A breaker which means you ought to limit current draw to 32A by code; you pulled 40A. Incidentally, I've used several of the Chinese relays in your EVSE in my OpenEVSE builds and while the relay claims to be 80A and EMW claims 60A, I find that these relays typically work well without overheating only up to 40-50A at best; the real problem is that these relays are variable and it's hard to predict which particular one will not get hot at 40A. Thirdly, there is no inherent danger of using a properly made L2 EVSE without current monitor display; there are plenty of commercial examples. In DIY openEVSE builds, the current should be firmware limited for hardware and outlet to be used. In this, this basic kit the fuses and relays are rated for 30A and so it should normally be set to a maximum of 24A (some have pushed it to 28-30A). If it is thus limited, it can be used safely in any circuit that will support 24A or more. There is, therefore, no added safety to having an LCD or adjustable button. Of course, I prefer to be able to change current even in a basic unit and think it would be very useful if Chris and others would implement an easy way to adjust current up to the max of the EVSE using a simple LED flash system like Phil does with the EVSEupgrade.dsinned said:This issue keeps coming up with respect to these so-called "basic" kits. Current limiting seems to be sort of a "moving target" especially for "portable" units.
Personally, I don't care for Tesla's solution with resistor mods to a couple of common AC adapters. These cost $50 each. WAY overpriced imho! Not to mention, an adapter for 32A was completely omitted. These are quite commonly required, although there is no standard for "40A" outlets. Thus, many EVSE users are violating code with 50A outlets on less amperage circuits. I'm guilty of that as well!
I became concerned about this, so I did a "controlled" experiment last weekend. I intentionally increased the current limiter on my EVSE from 32A to 40A, which is easy to do with a JuiceBox with key fob and LCD options. I was charging my RAV4 EV with its OBC that allows a maximum of 10kW (or 250V at 40A). I measured ~225V AC line voltage at the EVSE at this load, so I was really only drawing about 9kW from the wall. As it turns out this presented a false sense of security!
On a moderately warm day, it took a little over 60 minutes for a 40A rated circuit breaker to trip in my Main Power Distribution Panel on the outside of my house. I purchased that breaker from Home Depot earlier this year, so I know it was essentially new and good condition. From the 50A outlet to the output cable of the EVSE, surface temperatures were all warm to the touch but not of any real concern. My Juicebox's I/O cables are rated for 50A/40A respectively, and the AC outlet rated for 50A it was plugged in to.
By the time the CB tripped in the main distribution panel, it became VERY HOT; almost enough to burn my finger. Thankfully, it did its job, but I have no idea how hot the internal stranded copper wiring got from the breaker to the AC outlet, which is routed through the crawl space under the house and through a wall into my garage where that outlet is installed. I'd bet hot enough to be worrisome as I believe the dedicated wiring conductors are probably of insufficient gauge for a 40A continuous load. I wish I knew what the gauge size is for certain, but as I recall it is certainly not as large as 6AWG, which is recommended for a 50A outlet.
This points out the inherent danger of using an L2 EVSE without an output current monitor display. These basic DIY kits are all well and good for the lowest cost, bare bones EVSE, but I highly recommend adding an output current monitor display for safety sake. Plus, make certain your circuit breaker protection is appropriate for the household wiring and J1772 output cable you are using, especially if you are using a 50A AC outlet to plug in your EVSE. Which ever has the lowest amperage rating, should match the rating of the circuit breaker. This is something that NO EVSE can determine for you, or warn you when it becomes overloaded, so you have to physically check it yourself. When in doubt, hire a qualified Electrician!