I agree, I thought I had mentioned the cheap portable L2 EVSEs(like the Ebusbar) which are 16a and I was thinking of using on a 20a circuit, yes 20a circuit=16a continuous. Clipper Creek makes it easy as their model numbers indicate circuit required not output current, therefore if you have a 20a circuit then get the ClipperCreek with the 20 in it's model numberLeftieBiker said:12 gauge wiring can provide 20 amps, but as the maximum load, not the maximum sustained load. That gauge wiring would require a 16 amp EVSE, not 20 amp.
AntroX-True while 12 gauge wiring may be able to support 20a, something like a EVSE is rated as continuous duty and therefore subject to the 80% rule. Extension cords being freestanding and not in a wall(where they could trap heat) are generally rated 20a for 12g and 15a for 14 gauge. Breakers also can be an issue, a 20a breaker will get VERY warm and possibly trip running 20a continuous, they do make continuous rated breakers but they are very rare and by far not the norm. I regularly run 19a on a 20a breaker and the breaker itself gets very warm, I only do this for an hour or so and the wiring feeding the outlet is in metal conduit, lastly I do it with the breaker panel door open to dissipate the heat but it's not really a good practice to overheat a breaker in this manner Always better to error on the side of caution, especially for wiring built into the wall, don't want that to get hot and potentially burn down your house :shock: