Ingineer
Well-known member
You don't know that! How do you know the drop isn't coming before the panel? He didn't measure voltage drop on that circuit, only the TOTAL voltage sag of the whole system! The only valid way to measure voltage drop is to connect one meter lead to the bus bar in the panel, and then the other at the outlet hot terminal, then repeat for neutral. If this had a total 6.5v drop, I'd be very alarmed!smkettner said:BTW if it is a 20a breaker it must be #12 wire. I think code says 3% voltage drop max and you are exceeding that amount.
To lose that voltage in #12 wire the circuit would be over 175' so any shorter tells me the drop is in the connections.
Unless you are very experienced with electricity and qualified to work on exposed live connections, I don't advise removing the cover of the panel for this test. You could also conduct a more accurate and safer voltage drop test by finding an outlet on the same leg, but on a different breaker, and measuring from hot to hot, then neutral to neutral and summing the two. That would be a much more accurate drop reading, and without needing to be exposed to the dangerous live panel.
It's not uncommon to see the incoming connections at the panel sag a handful of volts under a heavy load such as 12A. This is caused by the meter, a potentially long run of service entrance (many are aluminum), and the transformer itself.
-Phil