From your answers and rereading your previous posts, I am guessing your installation is at home on a standard 120/240 circuit. If so, then you do not need the neutral for the 25IDS-N. Since that meter has internal CTs, the maximum wire diameter it will work with is about 3/8 inch. I don't know if you will be able to get the 2 AWG wire through its openings. If you are using standard type THHN or THWN building wire, it will be a tight fit. The alternative is the EKM Omnimeter which uses external donut current transformers and fused voltage inputs. There are different ways to connect it using either 1 or 2 current transformers and 1 or 2 voltage inputs. If you use 1 current transformer and 1 voltage, you do not need neutral. If you use 2 current transformers, then you need 2 voltage inputs which means you need the neutral. I suggest you download the manuals for the meters from EKM's web site and look at the different possibilities. There is a lot of good information there. If the conduit for your circuit has not been installed, why not go with one size larger and have the neutral pulled in? That would also allow you to have a NEMA 14-50 receptacle installed (instead of hard wiring) if a future EVSE required that type of connection.
Gerry