Sometimes you get similar capabilities stated different ways and so the results are confusing.
In US electrical code there is an "80%" rule saying don't draw continuous current more than 80% of the breaker / circuit capacity.
So a 40A circuit & breaker is needed for a device that can draw 32A.
A 30A circuit & breaker is needed for a device that can draw 24A.
(For the 2011 & 2012 LEAF, a 20A breaker is needed when using 16A.)
Many commercial locations are 208V, but many home locations are 240V.
So when you look at total kW used by charger, the voltage comes into play not just the amperage.
http://www.blinknetwork.com/file/296/OM0001_L2_R_WMv1.8.pdf" onclick="window.open(this.href);return false;
...blink EVSE’s factory default current setting is 30 amps...
So, for typical home use you have a 40A breaker, 32A continuous capable circuit, but the blink lowers it to 30A (probably due to the rating of the J1772 plug.) 30A*240V=7.2kW
LEAF currently has a "3.3kW" charger, but will reportedly offer a "6.6kW" in future? Why 6.6kW, not 7.2kW? Not sure, but 208V@32A=6.6kW.
In any case, if the EVSE is 30A or 32A, and the car's charger is 6.6kW or 7.2kW they should be able to "negotiate" the highest common denominator and charge at the max allowed. That is assuming 240V home power. If you have 208V commercial power, not sure if the amperage will be higher due to lower voltage, or if you will be stuck charging at a slightly slower rate.