I have two 110 volt circuits in my garage that are fed by a 10/3 buried wire.
As it comes into the garage, it goes into a 4" junction box where from one side circuit A leaves and from the other side circuit B leaves. Each circuit feeds separate things. On A are florescent lights, garage door opener, outside security light and two motion detector lights. Circuit B is for the charger that came with the Leaf. Both circuits share the common ground.
In the 200 amp circuit breaker panel in the basement there are two separate breakers, each 15 amps and labeled as Circuit A and the other one as Circuit B. They could be pulling from the same side of the incoming 220. I'd have to change them anyway if I were to install an 220 volt EVSE in the garage by putting in a double breaker.
I realize a 30 amp ESEV would be pushing things, even if there were to be no additional draw coming from the 110 circuit A and circuit B, as the 30 amp EVSE will draw about 27 amps, so I think I had better stay with a 20 amp EVSE, like the Clipper Creek.
If I do this, I plan on running 10/2 from the junction box, taking one lead from the hot red wire and the other from the hot black wire, (about a 30 foot run, ) to the other side of the garage where I would run it into a 20 amp breakered disconnect switch. From this disconnect switch I would wire the Clipper Creek or install a dryer female outlet for the male plug on the Clipper Creek. (I am thinking about making it portable so I could take it to my sons where he would install a similar outlet off his air conditioner. (Wouldn't run them both at the same time.)
Is it necessary to have a ground on the Clipper Creek? If so I could make the 30 foot run with 10/3, rather than 10/2 and pick up the ground from the neutral on the incoming 10/3.
Your thoughts?
Thanks.
As it comes into the garage, it goes into a 4" junction box where from one side circuit A leaves and from the other side circuit B leaves. Each circuit feeds separate things. On A are florescent lights, garage door opener, outside security light and two motion detector lights. Circuit B is for the charger that came with the Leaf. Both circuits share the common ground.
In the 200 amp circuit breaker panel in the basement there are two separate breakers, each 15 amps and labeled as Circuit A and the other one as Circuit B. They could be pulling from the same side of the incoming 220. I'd have to change them anyway if I were to install an 220 volt EVSE in the garage by putting in a double breaker.
I realize a 30 amp ESEV would be pushing things, even if there were to be no additional draw coming from the 110 circuit A and circuit B, as the 30 amp EVSE will draw about 27 amps, so I think I had better stay with a 20 amp EVSE, like the Clipper Creek.
If I do this, I plan on running 10/2 from the junction box, taking one lead from the hot red wire and the other from the hot black wire, (about a 30 foot run, ) to the other side of the garage where I would run it into a 20 amp breakered disconnect switch. From this disconnect switch I would wire the Clipper Creek or install a dryer female outlet for the male plug on the Clipper Creek. (I am thinking about making it portable so I could take it to my sons where he would install a similar outlet off his air conditioner. (Wouldn't run them both at the same time.)
Is it necessary to have a ground on the Clipper Creek? If so I could make the 30 foot run with 10/3, rather than 10/2 and pick up the ground from the neutral on the incoming 10/3.
Your thoughts?