MikeD said:
Two minor comments to OP:
1) I notice that the most current version (6/12) of the GE WattStation Wall Mount: Plug-in Version (model EVWSWBC) Installation Guide and also User Manual specify "Wall power receptacle with a weatherproof locking cover is required", whereas previous (07/11) versions of those manuals (older PDFs still linked to by Lowes at this time) only read "... is recommended.". In his pictures RCEV13 clearly has a cover over the receptacle (although locked would make it doubly secure, imo).
However, please ESPECIALLY note that the weatherproof locking cover is required regardless of whether the plug-in model is installed indoors or outdoors, i.e. it also serves the purpose of limiting ready access to the receptacle from children.
.
As far as I know, the weatherproof locking cover is required only on outdoor mounted units. (I haven't seen the specific document referenced by MikeD though, but I relied on this 2012 document https://docs.google.com/viewer?a=v&q=cache:kSwYrWY4F1AJ:www.geindustrial.com/publibrary/checkout/Brochures%257CDEA-533A%257Cgeneric+&hl=en&gl=us&pid=bl&srcid=ADGEEShp7NXV0nRE8cs1FENKH7_v9ywFPrVvCTlmbalW2rvmOHvHWyxcfDTMw3Omwqmcu6wHgD-cLSS0CoK3Ry5NHqL0uFprriF0-f0DJPeC0PdBzxdrwbgsONiA236a2iBCpJJ3FpYk&sig=AHIEtbRfd_TsCaXbgNKW5coEv9qnS0CIeg" onclick="window.open(this.href);return false; ) I spoke with one of the "big guys" there at GE, due to the fact that my Wattstation, which had been stored for many months, had some of the wires come loose during shipping, so he was helping to troubleshoot it, and in fact we easily restored it to working condition. He stated that the drawing was in fact for an outdoor location.
Also, as Rauv pointed out in a previous post helping me, http://www.mynissanleaf.com/viewtopic.php?f=26&t=11026&p=259265#p259265" onclick="window.open(this.href);return false; ,
"If your 6-50 receptacle is mounted outside and in a protected area from the elements (i.e damp locations, not wet location as defined in the NEC) then you need a weatherproof enclosure for your receptacle. Article 406.9 of the 2011 NEC reads as follows:
"406.9 Receptacles in Damp or Wet Locations - A receptacle installed outdoors in a location protected from the weather or in other damp locations shall have an enclosure for the receptacle that is weatherproof when the receptacle is covered (attachment plug cap not inserted and receptacle covers closed)."
As an additional detail, the mounting hardware has been changed for the 2012 version from 3/8" fasteners to 1/4" fasteners. I had heard that the 3/8" fasteners were slightly too big for the mounting bracket holes, but I don't know that for a fact as I followed the 2012 instructions and used 1/4" x 1 3/4" concrete hex screws (I chose stainless).
You might also want to note, as I had almost overlooked it, that the height from the floor to the
bottom of the mounting bracket should be 18" minimum for indoor use and 24" minimum for outdoor use. That keeps the installed unit at an ADA compliant height.