mctom987 said:
I see "Businesses use 208V" fairly often, and while that may be the service voltage, that's rarely what's hooked up.
Generally, 208V is provided in a 3-phase setup. Since most consumer and end-of-circuit equipment does not run on 3-phase supply, it must be changed. This 3-phase power is usually converted into 120V and 240V lines.
Commercial L2 chargers don't necessarily operate on 208V (although they very well could be), and are probably operating on 240V. Most people see about 5.8kW when charging on these L2 chargers. This isn't because 28A 208V is 5.8kW, it's because a 30-A circuit is limited to 80% continuous draw. This means 24A max power. 24A @ 240V = 5.76kW.
The J1772 connector on the Leaf is rated for 27.5A continuous. This is between 9 and 10 gauge wire. 27.5A @ 240V = 6600W, or, 6.6kW the Leaf is rated for. In order to supply this, you need at least a 40A circuit (as 35A #9 wires and equipment are quite rare), and a similarly rated 40A EVSE.
6.6kW charging rates are still possible on 208V, but this would require 32A supply on a 40A circuit, which the Leaf's charger and J1772 are not designed to handle. You would be limited to 5720W, or 5.72kW. This is very close to the 240V rate of 5.76kW. Because of this, it's likely impossible to guess/know the rating of the EVSE or voltage by the charging times or rates alone.
In the end, ~5.8kW is probably the fastest rates you will see on most commercial installations, unless there is a known high-power (70A, for example) EVSE installed.
The information that the J1772 is rate for 27.5A continuous is interesting and does agree with what I have observed but I cannot find that specification anywhere. I have seen figures given for the J1772 that say 30A, another put is at 32A, but I have not seen anyone put it at 27.5A. Would appreciate a link to where you saw 27.5 as the continuous current limit.
This does support the statement that charge power is current limited. With a home installation (Level 2 - single-phase 240v) and 27.5A that would give you 6.6kW.
With a business feed using 3 phase power you only get 208v and at 27.5A that comes to 5.72kW, which is about what I see when I charge at work.
(3 phase is used where a lot of power is distributed, like commercial buildings. Take a look at the bigger power transmission towers/lines and you will see there are 3 sets of wires. I Typically at commercial locations they do not use 240v. Equipment they use is designed for this voltage, motors will run on 3-phase 208v, etc. In fact, to get 240 they would need to put in transformers or more commonly use something called a buck-boost transformer).