2017 Leaf _EVSE Green light Blinking on Level One Charger with a Solar set up

Sun Aug 23, 2020 10:05 am

Hello, I own a 2017 Leaf. I have a solar Set up with a 2500 inverter. When I plug in I get a blinking green light.
Ive seen others with the same problem but I cant figure out what to do when reading past posts. My set up powers everything else ( fridge, freezers, etc)
So, Im getting this green blinking light. I have search all over and I get little results except for this " 1/2 watt, 100kohm resistor"
Or I get this " bonding ground-neutral with a resistor on some of the inverter-generator threads" Which I need help with..

Seeing I could get a successful solar set up going can some one please explain to me in layman's terms what am I supposed to o.
I have searched other links so please be patient.
I very much appreciate you help here. Im so close to using my off the grid system.
Thank you

coldstorage5
Posts: 23
Joined: Thu Nov 02, 2017 3:34 pm
Delivery Date: 08 May 2017

Re: 2017 Leaf _EVSE Green light Blinking on Level One Charger with a Solar set up

Sun Aug 23, 2020 6:07 pm

Is it the pure sine of modified sine issue?

LeftieBiker
Moderator
Posts: 15782
Joined: Wed May 22, 2013 3:17 am
Delivery Date: 30 Apr 2018
Location: Upstate New York, US

Re: 2017 Leaf _EVSE Green light Blinking on Level One Charger with a Solar set up

Sun Aug 23, 2020 7:34 pm

I have a solar Set up with a 2500 inverter.
First: What is the rated continuous and surge output of the inverter? I'm assuming that the "2500" doesn't stand for "2500 watt"...

Second: are you trying 120 volt charging, or 240 volt? L-2 240 volt charging is where issues with generators arise - L-1 120 volt usually works fine.
Scarlet Ember 2018 Leaf SL W/ Pro Pilot
2009 Vectrix VX-1 W/18 Leaf modules, & 3 EZIP E-bicycles.
BAFX OBDII Dongle
PLEASE don't PM me with Leaf questions. Just post in the topic that seems most appropriate.

GerryAZ
Gold Member
Posts: 2632
Joined: Mon Nov 22, 2010 6:47 pm
Delivery Date: 12 Jun 2011
Location: Phoenix, AZ

Re: 2017 Leaf _EVSE Green light Blinking on Level One Charger with a Solar set up

Sun Aug 23, 2020 9:38 pm

I assume you are trying to charge at 120 volts using the Nissan EVSE and a 2500 watt inverter. Most EVSE's, including that Nissan unit check for a proper equipment ground connection by injecting a small current from line to ground. The grounding test injection current from the Nissan EVSE is less than 5 mA so it will not trip a properly-installed and functioning GFCI, but it will not charge the car if the grounding test is not satisfied. Most portable generators are shipped from the factory with neutral isolated from ground so either a resistor between neutral and ground or a solid bonding jumper (there are advantages/disadvantages associated with either method) is needed to satisfy the EVSE. It is likely that the neutral of your inverter output is not referenced to ground so the EVSE will not charge. Check manufacturer instructions for your inverter to see if it can be configured with a neutral ground (either resistor or solid bond). Grounding the neutral may permanently damage some inverters so be careful. Also, I don't know if the EVSE and onboard charger would tolerate the stair step waveform from a "modified sine wave" inverter so I recommend that a "pure sine wave" inverter be used. I tested my 2011, 2015, and 2019 LEAF's with my portable generators which have pure sine wave inverter outputs. Both of my generators came from the factory with their neutrals isolated from ground, but the owner manuals allow for bonding, if required. I have used 100k ohm resistors and solid bonds for testing. The resistor will limit ground fault current to a safe level, but it will prevent tripping of a GFCI if a ground fault happens. The solid bond provides no ground fault protection, but it will allow a GFCI to function normally and trip for a ground fault beyond the GFCI. A solid neutral to ground bond is similar to a standard residential service entrance panel ground/bond connection.
Gerry
Silver LEAF 2011 SL rear ended (totaled) by in-attentive driver 1/4/2015 at 50,422 miles
Silver LEAF 2015 SL purchased 2/7/2015; traded 8/10/2019 at 82,436 miles
White LEAF 2019 SL Plus purchased 8/10/2019



Oilpan4
Posts: 1771
Joined: Wed Jan 09, 2019 10:51 pm
Delivery Date: 10 May 2018
Leaf Number: 004270

Re: 2017 Leaf _EVSE Green light Blinking on Level One Charger with a Solar set up

Thu Aug 27, 2020 11:27 am

coldstorage5 wrote:
Tue Aug 25, 2020 12:18 pm
https://www.youtube.com/watch?v=c2GqbM0JxlM

Do you think this will work?
Yes it should work and it's a bad idea.
"THE ABOVE POST CONTAINS MISLEADING AND INACCURATE INFORMATION. PLEASE CONSIDER IT OPINION, NOT FACT". -someone who I offended and is unable to produce the facts in question.

coldstorage5
Posts: 23
Joined: Thu Nov 02, 2017 3:34 pm
Delivery Date: 08 May 2017

Re: 2017 Leaf _EVSE Green light Blinking on Level One Charger with a Solar set up

Thu Aug 27, 2020 2:41 pm

Why a bad idea, can you please elaborate?
Thank you

Oilpan4
Posts: 1771
Joined: Wed Jan 09, 2019 10:51 pm
Delivery Date: 10 May 2018
Leaf Number: 004270

Re: 2017 Leaf _EVSE Green light Blinking on Level One Charger with a Solar set up

Thu Aug 27, 2020 7:46 pm

The inverter runs two 60 volt lines.
Depending on the inverter if you try to ground one of the 2 lines to make a neutral it could fry the inverter.
Also charging circuits don't like modified sine wave power.
"THE ABOVE POST CONTAINS MISLEADING AND INACCURATE INFORMATION. PLEASE CONSIDER IT OPINION, NOT FACT". -someone who I offended and is unable to produce the facts in question.