coulomb
Posts: 74
Joined: Thu Oct 09, 2014 5:08 pm
Delivery Date: 07 Mar 2015
Leaf Number: 200445
Location: Brisbane, Australia

Re: Help with wiring a NEMA 10-30P outlet!

Sat Nov 02, 2019 5:41 am

SageBrush wrote:
Sat Nov 02, 2019 4:58 am
^^ My electrician put red tape on the white wire he used for the second 'hot' connection.
Ah, so it's true! And tape, no less, which always seems to lose its stickiness after a few years. Excuse me while I adjust to the new (to me) reality... wow. What a weird world.
A yellow stripe is a good idea. I don't think I have noticed it on my wires.
It's one of those international standards. In my country, "international" has favourable connotations: standardization, the good of the world, working together towards a common goal, that sort of thing. I get the feeling that in the USA, not so much. My apologies if that's unkind or simply mistaken.
2012 Leaf with new battery May 2019. New to me June 2019.

SageBrush
Posts: 4907
Joined: Sun Mar 06, 2011 2:28 am
Delivery Date: 13 Feb 2017
Location: NM

Re: Help with wiring a NEMA 10-30P outlet!

Sat Nov 02, 2019 6:04 am

coulomb wrote:
Sat Nov 02, 2019 5:41 am
SageBrush wrote:
Sat Nov 02, 2019 4:58 am
^^ My electrician put red tape on the white wire he used for the second 'hot' connection.
Ah, so it's true! And tape, no less, which always seems to lose its stickiness after a few years. Excuse me while I adjust to the new (to me) reality... wow. What a weird world.
A yellow stripe is a good idea. I don't think I have noticed it on my wires.
It's one of those international standards. In my country, "international" has favourable connotations: standardization, the good of the world, working together towards a common goal, that sort of thing. I get the feeling that in the USA, not so much. My apologies if that's unkind or simply mistaken.
.
I'd say that the local message is "don't rely on the wire color."
2013 LEAF 'S' Model with QC & rear-view camera
Bought off-lease Jan 2017 from N. California
Two years in Colorado, now in NM
03/2018: 58 Ahr, 28k miles
11/2018: 56.16 Ahr, 30k miles
-----
2018 Tesla Model 3 LR, Delivered 6/2018

jjeff
Posts: 1995
Joined: Wed Jan 13, 2016 9:10 am
Delivery Date: 13 Jul 2014
Leaf Number: 422121
Location: MSP MN

Re: Help with wiring a NEMA 10-30P outlet!

Sat Nov 02, 2019 6:57 am

Sage is correct, it's done somewhat regularly if they are repurposing a white wire(for example going from a 120v circuit that used the white wire to a strictly 240v circuit that needs another hot but no white/neutral). They use a quality(generally 3M) colored tape(electricians always carry a supply of colored tape on their cart) and wrap it several times around the white insulation on both ends near the connections. Wrapped several times it's not going to come off even if the tape loses its stickiness and you NEED to know this white wire is a home run(not shared by any other circuits or spliced in a box anywhere between the panel and outlet. I'm pretty sure but not positive a green wire cannot be repurposed, it always needs to be ground. Not sure if say a black wire can be repurposed to a white wire, I'm sure a real electrician will know.
Now what I've occasionally done besides using the tape is to use a red or black sharpie type of permanent marker to also color the white wire the correct color, figure it can't hurt and anything to draw attention that the wire is no longer a neutral. I kind of agree that the neutral should have been black or the color of our negative wire in DC circuits but maybe they wanted to differentiate between AC and DC where in DC ground is black and hot red. As mentioned our AC uses white for neutral, generally black hot and often red for the second hot but can also be used in 120v circuits and lots of other colors(yellow, orange, etc.) for other hots.
2012 SL purchased used 2/'16
2013 S w/QC purchased new
Juicebox Premium 60a L1/L2 EVSE, Ebusbar 16a L1/L2 EVSE
'12 EVSEupgrade'd 20a L1/L2 EVSE, '13 EVSEupgrade'd adjustable 6-20a L2, 6-13a L1 EVSE
Zencar 13, 20, 30a L1/L2 portable EVSE
GE Durastation 30a

User avatar
Nubo
Posts: 5461
Joined: Fri May 28, 2010 11:01 am
Delivery Date: 31 Oct 2014
Location: Vallejo, CA

Re: Help with wiring a NEMA 10-30P outlet!

Sat Nov 02, 2019 9:37 am

coulomb wrote:
Sat Nov 02, 2019 4:34 am

BTW, is it true that you actually have pure green ground wires in places? The extra cost of the yellow stripe to pander to color blind people is outrageous?
Either green or bare Copper. The Earth still manages to wobble about its axis, somehow.
I noticed you're still working with polymers.

LeftieBiker
Moderator
Posts: 13498
Joined: Wed May 22, 2013 3:17 am
Delivery Date: 30 Apr 2018
Location: Upstate New York, US

Re: Help with wiring a NEMA 10-30P outlet!

Sat Nov 02, 2019 12:28 pm

Last year I was watching an ep of This Old House, in which an electrician installed a charging station for an EV. He used a white wire as the second Hot, and didn't bother to re-label it. That's "felony stupid" in my book.
Scarlet Ember 2018 Leaf SL W/ Pro Pilot
2009 Vectrix VX-1 W/18 Leaf modules, & 3 EZIP E-bicycles.
BAFX OBDII Dongle
PLEASE don't PM me with Leaf questions. Just post in the topic that seems most appropriate.

Oilpan4
Gold Member
Posts: 958
Joined: Wed Jan 09, 2019 10:51 pm
Delivery Date: 10 May 2018
Leaf Number: 004270

Re: Help with wiring a NEMA 10-30P outlet!

Sun Nov 03, 2019 8:08 am

I have only seen a hand full of correctly installed dryer circuits over the last 15 years.
Usually the only ones wired correctly are the 4 prong, 4 wire 14-30 outlets.
I don't think I have even seen a properly marked 2 insulated wire (black/white) with a bare ground wire romex or triplex cable used on a 240v circuit properly marked unless I put it there.
2011 white SL leaf with 2014 batt.
Chargers: Panasonic brick moded for 240v, duosida 16a 240v and a 10kw setec portable CHAdeMO
Location: 88103

goldbrick
Posts: 642
Joined: Tue Aug 01, 2017 3:33 pm
Delivery Date: 01 Aug 2017
Leaf Number: 311806
Location: Boulder, CO

Re: Help with wiring a NEMA 10-30P outlet!

Sun Nov 03, 2019 10:30 am

Oilpan4 wrote:
Sun Nov 03, 2019 8:08 am
I don't think I have even seen a properly marked 2 insulated wire (black/white) with a bare ground wire romex or triplex cable used on a 240v circuit properly marked unless I put it there.
Ditto for me. I have to confess though...even when I've re-wired some of my own 240V circuits I didn't bother to mark the white wire as a hot. It's my house and it's obvious that the outlet and breaker are 240V so it is hard to forget that it's a 'hot' wire.

As for the US NEC rules for wire colors, my understanding is as follows:

For wire sizes <= 6 AWG

ground wires are green or bare copper. Green colored wires cannot be remarked for any other use, regardless of size.
neutral wires are white or gray, or a base color with 3 continuous white stripes
any other color (not green, white or gray) is a hot wire

For wire sizes 4 AWG and larger, wires that aren't green or white can be remarked since as Henry Ford said, you can get this size wire in any color you want as long as it is black.

Oilpan4
Gold Member
Posts: 958
Joined: Wed Jan 09, 2019 10:51 pm
Delivery Date: 10 May 2018
Leaf Number: 004270

Re: Help with wiring a NEMA 10-30P outlet!

Sun Nov 03, 2019 10:56 am

Watch out for gray wires.
The only time I have encountered them is where multiple circuits share a neutral.
They are a pain to completely deenergize.
So you turn it off, unwired the neutral, it sparks as it disconnects and lights some where else go out.
Now you have a live energized neutral to work around.
2011 white SL leaf with 2014 batt.
Chargers: Panasonic brick moded for 240v, duosida 16a 240v and a 10kw setec portable CHAdeMO
Location: 88103

LeftieBiker
Moderator
Posts: 13498
Joined: Wed May 22, 2013 3:17 am
Delivery Date: 30 Apr 2018
Location: Upstate New York, US

Re: Help with wiring a NEMA 10-30P outlet!

Sun Nov 03, 2019 12:57 pm

I have to confess though...even when I've re-wired some of my own 240V circuits I didn't bother to mark the white wire as a hot. It's my house and it's obvious that the outlet and breaker are 240V so it is hard to forget that it's a 'hot' wire.
Houses get sold or passed down to kids.
Scarlet Ember 2018 Leaf SL W/ Pro Pilot
2009 Vectrix VX-1 W/18 Leaf modules, & 3 EZIP E-bicycles.
BAFX OBDII Dongle
PLEASE don't PM me with Leaf questions. Just post in the topic that seems most appropriate.

goldbrick
Posts: 642
Joined: Tue Aug 01, 2017 3:33 pm
Delivery Date: 01 Aug 2017
Leaf Number: 311806
Location: Boulder, CO

Re: Help with wiring a NEMA 10-30P outlet!

Sun Nov 03, 2019 9:22 pm

Houses get passed down but more importantly, people live in them. I would never do anything half-a$$ when it comes to wiring a house and I don't condone anyone else doing it either. However, I'd guess that 99% of the 240V household circuits that use romex (NM-B) cable for the 240V circuits use black and white wires for the 2 hots and the white wire is not re-marked with another color. I just passed an electrical inspection on some work I did on my house and that point was never mentioned, even though I did the exact same thing. This wiring method is common to the point of being a de facto standard although technically, I think it does not meet code. There may be an exception in the code for this situation that I'm not aware of but my understanding is that the white wire of a 240V circuit should be re-identified with tape or other marking to indicate it is an ungrounded conductor. But virtually no one (except Oilpan) does that.